I noticed a few days ago that our gas boiler was short cycling. Burner comes on for 1-2 mins, cycles down and shuts off.... Just for it to immediately get another call for heat and turn back on again. .. It does this over and over and never turns off long enough for the zone valve to close or pump to turn off.
I've narrowed this down to the Hot Water. When I turn off the HW at the programmer, the short cycling stops.
Checked CH independently of HW and CH is working fine.
At first I thought it could be the HW zone control valve staying stuck open (or at least the end circuit remaining closed), but if that was the case, switching off the HW at the programmer wouldn't have any affect - right? If its stuck open, the programmer wouldn't have any influence over it any more.
This now makes me think it's the cylinder stat. Stat not satisfied so it keeps calling the boiler. The boiler stat is quickly satisfied so shuts off, just for the cylinder thermostat to switch it back on.... And so on and on and on. Thoughts?
Take the cylinder stat out of the equation (by turning it off at the programmer) and the issue stops.
Tested the theory by turning up cylinder stat and letting it run until boiler turned off (so cylinder full of freshly heated water). Turned off HW at programmer and lowered temp on cylinder stat right down - so stat set lower than the water in the cylinder.
My view here being, if stat is working OK, the freshly heated water in the cylinder is hotter than the new stat level, so it shouldn't immediately demand heat........ Right?
Turned on HW at programmer again and low and behold, the boiler is met with an immediate demand for heat.
Stat issue?
Any other checks I could do?
Any other ideas of what it might be?
New to the forum so please be gentle
I noticed a few days ago that our gas boiler was short cycling. Burner comes on for 1-2 mins, cycles down and shuts off.... Just for it to immediately get another call for heat and turn back on again. .. It does this over and over and never turns off long enough for the zone valve to close or pump to turn off.
I've narrowed this down to the Hot Water. When I turn off the HW at the programmer, the short cycling stops.
Checked CH independently of HW and CH is working fine.
At first I thought it could be the HW zone control valve staying stuck open (or at least the end circuit remaining closed), but if that was the case, switching off the HW at the programmer wouldn't have any affect - right? If its stuck open, the programmer wouldn't have any influence over it any more.
This now makes me think it's the cylinder stat. Stat not satisfied so it keeps calling the boiler. The boiler stat is quickly satisfied so shuts off, just for the cylinder thermostat to switch it back on.... And so on and on and on. Thoughts?
Take the cylinder stat out of the equation (by turning it off at the programmer) and the issue stops.
Tested the theory by turning up cylinder stat and letting it run until boiler turned off (so cylinder full of freshly heated water). Turned off HW at programmer and lowered temp on cylinder stat right down - so stat set lower than the water in the cylinder.
My view here being, if stat is working OK, the freshly heated water in the cylinder is hotter than the new stat level, so it shouldn't immediately demand heat........ Right?
Turned on HW at programmer again and low and behold, the boiler is met with an immediate demand for heat.
Stat issue?
Any other checks I could do?
Any other ideas of what it might be?