The ring final it not so cut and dried, the idea is to stop 2.5 mm cable which is rated around 20 amp from getting a load over its rating, there is a picture in the BS7671 which shows the options which if used will reduce the likelihood of an overload to acceptable limits, two sockets can deliver 26 amp (2x13) but in the main it will not supply over 20 amp average over an hour so a double socket on a spur is permitted, with a 100 meters of cable in a ring final, sockets need the consumer unit can overload one leg, so there are rules like fixed appliances over 2 kW should have a dedicated supply, as portable items will be unlikely to overload the system for long.
So a kettle will likely only be used for 5 minutes, where a tumble drier is used for maybe 1½ hours, so kettle does not need a dedicated supply, and a tumble drier would need a dedicated supply if otherwise it would load one end of the ring final, but if at centre of ring final not really a problem. But an immersion heater which could run for 3 hours clearly needs a dedicated supply.
There has been some discussion on figure of 8, I was told when doing my C&G2391 to test to see if there was a figure of 8 and list it as a fault, however I can't find a regulations to say it must not be used, however the ring final is a bit of an odd one out, and the appendix shows most options and does not show fig of 8, as to if the appendix is part of regulations is also in debate, however to get the C&G certificate one is tested with questions from the appendix, so it seems it is part of regulations.
I don't have the circle to hand, I am sure some one will post the page, which shows what it permitted, to be frank can't quite work out what you are trying to do.