Shared Neutral Current Additive 120/208?

Discussion in 'Electrics Outside of the UK' started by donniet1977, 9 Dec 2013.

  1. donniet1977

    donniet1977

    Joined:
    9 Dec 2013
    Messages:
    5
    Thanks Received:
    0
    Location:
    California
    Country:
    United Kingdom
    I'm remodeling my kitchen and am bringing it up to code. My service is 120/208. I wired up my first multiwire circuit. I decided to read neutral current flow with a clamp on ammeter to make sure everything was cool. I had a 1 amp load and a 2 amp load on the two hots. I expected to see something less than 2 amps on the neutral but was surprised to see the full 3 amps. The hots are fed from opposite busses. Can anyone help me figure this one out?


    Thanks,

    Don
     
  2. Sponsored Links
  3. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,493
    Thanks Received:
    403
    Location:
    Devon
    Country:
    United Kingdom
    Must be on the same phase (hot line).
     
  4. donniet1977

    donniet1977

    Joined:
    9 Dec 2013
    Messages:
    5
    Thanks Received:
    0
    Location:
    California
    Country:
    United Kingdom
    Nope. 208V between the two.
     
  5. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,493
    Thanks Received:
    403
    Location:
    Devon
    Country:
    United Kingdom
    Then your clamp meter is wrong.

    What loads are these?
     
  6. Sponsored Links
  7. donniet1977

    donniet1977

    Joined:
    9 Dec 2013
    Messages:
    5
    Thanks Received:
    0
    Location:
    California
    Country:
    United Kingdom
    Refrigerator at 1 amp and 3/8" drill motor at 2 amps. I was using a cheap off brand clamp on ammeter but it doesn't seem that would be the culprit here. I might have to increase load and test again.
     
  8. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,493
    Thanks Received:
    403
    Location:
    Devon
    Country:
    United Kingdom
    You could run into odd readings at low loads, and also with inductive/capacitive loads too. Many cheapy clamp meters are no good at low currents. There are also harmonic currents to consider.
     
  9. donniet1977

    donniet1977

    Joined:
    9 Dec 2013
    Messages:
    5
    Thanks Received:
    0
    Location:
    California
    Country:
    United Kingdom

    After more thorough testing I am even more troubled.

    Quick recap: My service 120/208, hot to hot is 208.

    With an 8.5 amp toaster oven on one circuit and 11 amps on the other circuit which feeds the fridge (about 1 amp) and space heater (temp) my neutral current reads 19.2 amps. I'm using an Amprobe ACD-15 Pro clamp on ammeter. This condo has been wired with mostly MWBCs ever since it was built from what I can tell. Have the neutrals been overloaded the whole time?! I'd really like to get on the feed to my panel which is just a subpanel but I just don't have the room.



    Thanks,

    Don
     
  10. donniet1977

    donniet1977

    Joined:
    9 Dec 2013
    Messages:
    5
    Thanks Received:
    0
    Location:
    California
    Country:
    United Kingdom
    I'm both embarrassed and happy to say that after further troubleshooting I discovered that the outlet we wired temp for testing was miswired and being fed by the wrong circuit. This led to all loads being on the same leg. I was a little lazy in my initial troubleshooting and made too many assumptions. One assumption was that there was a problem in the first place.

    I think the initial problem I saw with the 3 amp neutral was simply due to low inductive loading along with meter creep.

    Final Reads Ignoring Fridge (<1 amp) which is always on:

    CKT 1 on 2 off - In=9.1A
    CKT 1 off 2 on - In=11.9A
    Both CKTs on - In=12.0A

    Thanks for the replies.
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page