We have a 8.5kw shower on 6mm cable on a 32A type 2 Breaker, I know this is not correct, the breaker is two small and while 6mm is seen as borderline for 8.5kw, the cable run is fairly long, and does go through a bundle and some tight spots, so thats not really right either.
Soon that shower is going to be removed, and another 8.5kw shower fitted in a different bathroom (main shower is to be replaced with pumped shower), I don't think it would be right to use the existing cable for this, howwever here comes the problem
The house is a bungalow and while most of it is covered by a loft, the kitchen isn't, guess where the cu is...
so I can only see two ways to get a thicker cable to the cu
1) Twin and earth in some kind of trunking boxing in near the ceiling to a point where it can enter the loft, however this involves going around a corner and the permittable bend radius might cause problems here?
2) SWA on the outside, then into the loft, bend radius might be a problem again if its got to go through a hole in the wall, and how would it connect to the cu (plastic casing), would it have to go into some kind of box, then have twin and earth leaving the box and into the cu, and I guess the same the other end before it goes to the shower isolater?
32A type 2 breaker would have to be replaced with 40A type b one, (its already in the RCD side of the CU), so there wouldn't be a problem on that front.
Im thinking it might be better to have an electrician sort it all out, but the decision to do so does not come down to me, it comes down to my dad, and he has the opinion that it has been alright for 5 years...etc..you know the thing
Adam
Soon that shower is going to be removed, and another 8.5kw shower fitted in a different bathroom (main shower is to be replaced with pumped shower), I don't think it would be right to use the existing cable for this, howwever here comes the problem
The house is a bungalow and while most of it is covered by a loft, the kitchen isn't, guess where the cu is...
so I can only see two ways to get a thicker cable to the cu
1) Twin and earth in some kind of trunking boxing in near the ceiling to a point where it can enter the loft, however this involves going around a corner and the permittable bend radius might cause problems here?
2) SWA on the outside, then into the loft, bend radius might be a problem again if its got to go through a hole in the wall, and how would it connect to the cu (plastic casing), would it have to go into some kind of box, then have twin and earth leaving the box and into the cu, and I guess the same the other end before it goes to the shower isolater?
32A type 2 breaker would have to be replaced with 40A type b one, (its already in the RCD side of the CU), so there wouldn't be a problem on that front.
Im thinking it might be better to have an electrician sort it all out, but the decision to do so does not come down to me, it comes down to my dad, and he has the opinion that it has been alright for 5 years...etc..you know the thing
Adam