I've come across a couple of snippets recently while I've been investigating the best way to rewire my house:
(1) PC computers typically leak 3-5mA to earth during normal operation.
(2) A circuit should not have normal earth leakage of more than 1/3 the level of any RCD protection
Adding these together, it seems that putting more than 3 computers on a 30mA RCD system is against regs. If all the sockets share a single RCD at the CU, then this puts a limit on the number of PCs you can run in a house.
So, questions are:
(1) Are my `facts' correct?
(2) Has anyone had their household RCD pop due to too many computers?
(3) If you don't want to have unprotected sockets (and have more than 3 PCs), is splitting off one (or more) of the circuits onto a separate 30mA RCBO the best way to go?
(4) Does running the computers via UPS systems make any difference to the earth leakage?
(5) Do other items (e.g. TV) leak to earth in this way?
(1) PC computers typically leak 3-5mA to earth during normal operation.
(2) A circuit should not have normal earth leakage of more than 1/3 the level of any RCD protection
Adding these together, it seems that putting more than 3 computers on a 30mA RCD system is against regs. If all the sockets share a single RCD at the CU, then this puts a limit on the number of PCs you can run in a house.
So, questions are:
(1) Are my `facts' correct?
(2) Has anyone had their household RCD pop due to too many computers?
(3) If you don't want to have unprotected sockets (and have more than 3 PCs), is splitting off one (or more) of the circuits onto a separate 30mA RCBO the best way to go?
(4) Does running the computers via UPS systems make any difference to the earth leakage?
(5) Do other items (e.g. TV) leak to earth in this way?