Re the Honeywell zone valves. With the valve de energized, the "manual" lever can be pulled across against a fairly stiff motor resistance and then pushed up and latched almost fully open, this (on Honeywells), does not fire the boiler, its main purpose is to manually open the valves when draining/filling the system. If the valve is then energized the motor will drive the valve very fully open, the lever will fall down out of its latch, the auxiliary end switch in the actuator will then close to fire the boiler, when the valve is de energized then the valve will reclose because its no longer latched in.
Next time the droning is at its worst, ensure both zone valves de energized, then fire up the boiler on heating (rads) only, see does the noise return, if not, manually latch open the HW zone valve and check for noise.
Next time the droning is at its worst, ensure both zone valves de energized, then fire up the boiler on heating (rads) only, see does the noise return, if not, manually latch open the HW zone valve and check for noise.