Vibrating/ droning sound since new hot water cylinder was installed.

Checked the air vent is slacked off, The lockshield valve has an outer collar, you probably new that a radiator key is too small. I don’t want to damage the outer brass collar anymore, it’s already slightly bent. I’ve order a 4 way utility key that comes today. Can you tell me, If adjusting this valve stops the noise, can I leave this lockshield valve like that long term ? Or is this a temporary solution, in which we need a ABV installed going forward? Typically it hasn’t vibrated/ droned much in the short time I’ve been at home this week; but I’m here home most of tomorrow, with my new 4 way key!
 
Checked the air vent is slacked off, The lockshield valve has an outer collar, you probably new that a radiator key is too small. I don’t want to damage the outer brass collar anymore, it’s already slightly bent. I’ve order a 4 way utility key that comes today. Can you tell me, If adjusting this valve stops the noise, can I leave this lockshield valve like that long term ? Or is this a temporary solution, in which we need a ABV installed going forward? Typically it hasn’t vibrated/ droned much in the short time I’ve been at home this week; but I’m here home most of tomorrow, with my new 4 way key!
A ABV installation is still recommended even if the boiler (like yours?) has a internal one, to cool down the boiler heat exchanger but if there is no banging/noise from the boiler on pump overrun when it shuts down without it, maybe leave it.
 
Update on the return pipe spindle:


Hi again,
Thanks for the advice. I managed to turn the spindle on the return pipe using my smallest pliers (the 4-way key wouldn't fit). I marked the original starting position with a pink marker pen so I wouldn't lose my place.
Here is what happened:
  • I managed to turn it one full turn clockwise. As it got tighter, it started making a much louder water-flowing/rushing noise, likely because it was nearly closed off.
  • Because it was getting stiff to turn with the pliers, I backed it off anticlockwise until that rushing sound stopped.
  • I ended up leaving it half a turn more clockwise (closer to closed) than where I originally started.
The result: The drone did come back briefly later that evening, but it was much milder and only lasted for a few seconds.
Am I on the right track here? Should I try to close it down a bit further using the pliers to see if the drone stops completely, or does this indicate a different issue with the valve or balance?
 
The result: The drone did come back briefly later that evening, but it was much milder and only lasted for a few seconds.
Am I on the right track here? Should I try to close it down a bit further using the pliers to see if the drone stops completely, or does this indicate a different issue with the valve or balance
Yes, just adjust until the noise stops, then monitor for a bit.

If it all works as expected then job done.
 
Update
A different heating engineer was here today to service the boiler (he installed the boiler about 6 years ago.)
He had a look at the cylinder and said it definitely should have an automatic bypass valve.
It started to drone slightly, unbeknown to me, he took the brass collar off of the lockshield gate valve and adjusted it with his fingers, it stopped instantly. It hasn’t made a noise all evening . He said ideally, I should have a ABV fitted.
He also changed my programmer, so I can now have my hot water and central heating on separate times. So my hot water is now on 3 times a day for 30 minutes…Thanks for all the help everyone!
 

Attachments

  • IMG_1413.png
    IMG_1413.png
    1,001.8 KB · Views: 14
I’ve been trying to my head round this. Our plumber who I’ve since discovered is not Gas safe & we now question if he is G3 qualified installed our new hot water cylinder back in August. We had few issues, two leaks, (one from the top, one from the lockshield gate valve and a horrendous loud intermittent droning/virbration sound. He tried a couple of things to stop the noise, fixed the first leak. He replaced a 2-port valve, (another £180) but noise persisted. It was when I joined this forum I learnt that my system needed an ABV. Which indeed it did. The installer started to ignore my messages. Eventually the heating engineer who installed our boiler, also said it needed an ABV. Which he then installed, he also fixed the leak from the gatevalve. we haven’t had an issues since. However I then thought I’d check that the ghosting plumber had registered my cylinder as promised to the manufacturer for warranty. He hadn’t ‍ loosing faith further, once I’d discovered this, I tried to find him on the competent person scheme website, (not on there) then searched on our local council building regulations. No notification… I even emailed Building regulations and they confirmed that there was no notification on of a hot water cylinder at my address. I then messaged him to ask, if we could have the appropriate paperwork to make sure our house insurance was legitimate with the installation. He replied, not knowing what I’ve learned, with searches and emails, he says he will drop it round asap. But I think I’m right in thinking, if he’s not on a scheme and building regulations have had no notification. There is no way on earth he is able to drop me round a Building Regulations compliance certificate ! I have been told that I need to get a G3 qualified engineer to do a safety check and report on my new hot water cylinder system. Which will suffice and ensure that our home insurance will be happy. Is it possible that he’s G3 qualified and on a scheme that I’m not aware, still self certify and bring the certificate round? My husband certainly thinks so.
 
Is it possible that he’s G3 qualified and on a scheme that I’m not aware, still self certify and bring the certificate round?
It's not impossible but highly unlikely, or he would have done it by now.

It doesn't have to be someone on a competent person scheme, but as your LABC know nothing about it then it hasn't been notified.
 