As has been observed before, although that is probably not unreasonable, although you very frequently quote those figures, I have never seen them mentioned, or written down, by anyone but you!With a ring final with standard 32A MCB you consider it to have 20A drawn in centre and 12A even spread so the amps used to calculate are 26A not 32A.
If there is a double socket at the end, then you don't really have any choice but to do that, since it is then quite possible that there could be a 20A load right at the end. If it were only a single socket at the end, you could theoretically get more precise in calculating the 'worst case scenario' of VD, but I personally wouldn't bother.But do I assume a full 20amps of load lumped at one end?
The OP is talking about a 20A radial circuit. If there were 'heavy loads' close to the origin of such a circuit, they would have relatively little impact on VD (as observed at any socket), because of the short cable lengths.If you are that worried then use 4 mm² between CU and the cluster of heavy loads on the shorter side of the ring. Or use 4 mm² for the whole ring and thus reduce voltage drop for all soickets.