Hi all,
I have a small B&B with 8 rooms and have started to get complaints about the showers. I'm going to get someone in to do any work needed but wanted to work out what's going on.
I have a vented HW system that is fed from a tank in the loft of a 3 story building and a pump that circulates the HW around the building. Complaints started about 2 months ago and are usually about the showers on the top floor. I also noticed that about a month ago the pump started to make intermittent noise. Sounded like an engine revving or a light airplane flying over. If I turned the pump off and then back on again then the noise would stop most times.
To check if the pump was working I done the following:
With the boiler on but the pump off, I felt the hot water pipe (part of the loop, not a take off to a tap) on the top floor. It was cold.
I turned the pump on, waited 1 minute and felt the same pipe again. It was warm. There had been no outlets open so I guess that the pump is pushing the hot water around the loop ok.
Next, I took the showerhead off of one of the showers that I receive the most complaints about. I filled up a 2L bottle, 3 times and times each run.
The average fill time with the pump on was 30 seconds.
The average fill time with the pump off was also 30 seconds.
I was expecting there to be more flow with the pump on. I guess my question is:
Should the hot water circulating pump increase the flow rate when it is turned on?
Thanks,
Matt
I have a small B&B with 8 rooms and have started to get complaints about the showers. I'm going to get someone in to do any work needed but wanted to work out what's going on.
I have a vented HW system that is fed from a tank in the loft of a 3 story building and a pump that circulates the HW around the building. Complaints started about 2 months ago and are usually about the showers on the top floor. I also noticed that about a month ago the pump started to make intermittent noise. Sounded like an engine revving or a light airplane flying over. If I turned the pump off and then back on again then the noise would stop most times.
To check if the pump was working I done the following:
With the boiler on but the pump off, I felt the hot water pipe (part of the loop, not a take off to a tap) on the top floor. It was cold.
I turned the pump on, waited 1 minute and felt the same pipe again. It was warm. There had been no outlets open so I guess that the pump is pushing the hot water around the loop ok.
Next, I took the showerhead off of one of the showers that I receive the most complaints about. I filled up a 2L bottle, 3 times and times each run.
The average fill time with the pump on was 30 seconds.
The average fill time with the pump off was also 30 seconds.
I was expecting there to be more flow with the pump on. I guess my question is:
Should the hot water circulating pump increase the flow rate when it is turned on?
Thanks,
Matt