Working on a boiler today, live to neutral 240v, live to earth 240v, Earth to neutral 0v

On turning the isolator switch off and removing the fuse, at the boiler my readings were now:
Live to neutral 306v
Live to earth 70v
Neutral to earth 348v

Any ideas what would cause this one? Not for me to fix, told the guy to get an electrician, but very curious as I normally have a fair idea with odd voltage readings
 
Sponsored Links
Assuming it was high impedance digital meter these stray voltages are almost always induced from adjacent wiring or pipe work by capacitive coupling.

A useful tool is a low wattage 240 volt test lamp ( incandescent filament lamp ) to sink any induced current while measuring the voltage. Or invest in a low impedance meter.

Source of the stray voltages ? How many electrical phases in the building ( flats on different phases ) ? Plastic water pipes ?
 
Thanks for the response. It was a standard basic fluke multimeter I was using. Single phase new build type building (15 years old approx

Copper pipes off of boiler, but more often than not change to plastic outside of view in these type of houses
 