Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
(a)Gravity HW with pumped CH.or
(b)Fully pumped with 3 port mid position valve.or
(c)Fully pumped with two 2 port motorised valve
With (a) room stat will control the circulating pump.
With (b) room stat controls the valves movement and power output to fire boiler in CH position.
With (c) room stat will control the CH valve only and provide power to fire boiler.
First thing in all cases is to check output from room stat before moving on to the valves or the pump in case (a)
Defrosted the outside pipe after talking to British Gas on their website,pressed reset,boiler came on but thermostat does not light up,and boiler will not start from it so I am using the overide to get the heating on. Have changed the batteries on the thermostat any ideas, thanks.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local