As already said by HG looks like the diverter is passing.


eccoboy said:Flow rate is 9 litres per min
Cold water temperature is 10c
Hottest water running at 9 litres per min is just 39c
Cheers Ben
eccoboy said:Actually, yes, the heating pipe out does get hot, does that help?

Agile said:eccoboy said:Flow rate is 9 litres per min
Cold water temperature is 10c
Hottest water running at 9 litres per min is just 39c
Cheers Ben
Hang on folks, you have all read this and then gone on to suggest other faults!
A 24 kW boiler can heat 9.3 litres/minute through 35° C.
He has 9 li/min raised 39°C.
In my view this boiler is performing exactly as it should do !
I had exactly the same complaint from a customer today. Its all because the incomming water is colder than it used to be.
Tony