3 phase current
18 Feb 2009
Afternoon everyone,
Trying to remember how to specify cable for a three phase motor.
Motor rated at 6kVA.
6000 VA /230 V = 26.1 A
26.1 A/ 3 = 8.7A.
Am I right in thinking that each phase will carry 8.7A, and so the (3+E) cable must be spec'd to carry 8.7 A ?
Seems too simple to be true...
Cheers Garymo,
Apart from using the wrong voltage & forgetting to squareroot the 3, I was correct.
Memory is not what it used to be. Coincidence that my (incorrect) method gives very nearly the right answer - two wrongs almost making a right...
Thanks, David
I thought so - pretty darn close!
Obviously you worked out that V in this case is 400.
Would you not only need the PF if the power was quoted in kW?
I was only asking because motors are normally rated in watts/kW or in old money horse power. I was just wondering how he arrived at 6kVA.
4.8kW @ 0.8PF?
Stunlawless got the right answer because there's nothing wrong with his calculation! Think of his method as considering the load being shared equally by three 230V single-phase supplies, which is basically what a 3-phase supply is. :)
230 x (sqrt 3) = 398.37
close enough to spit on...
and it's
VA / V / Sqrt 3... not VA / ( V x Sqrt 3 )
OK...try the same with 80kVA and see what you get!