It was done to lengthen the tails. He did want a 100A in there but couldn't get one at short notice. Is it just a question of putting one in?
Here's a PIC:
Here's a PIC:
No, a standard 30mA must be used.If the cables are buried in the wall then you should have a time delayed RCD.
No, a standard 30mA must be used.If the cables are buried in the wall then you should have a time delayed RCD.
That may be so, nevertheless...Which would cause the whole house to loose power in the event of a fault.No, a standard 30mA must be used.If the cables are buried in the wall then you should have a time delayed RCD.
Also against the regs
Quite so.Different cable should have been used if its buried.
They are not in the wall, they are exposed right now but will be put in trunking or more likely boxed in and plaster boarded when the kitchen is done. What about the 63A isolator, I notice the new CU is indeed a 100A main switch.