Slug said:The problem comes about when the hot water is turned off.
The diverter valve closes and the hot system water in the plate heat exchanger is sat there chucking all its heat into the domestic side of the Plate Heat Exchanger. This causes the domestic water to get rather hotter than it should be and a PHE full of overheated domestic water will be in the pipework if the tap is re-opened before the PHE cools down.
A giannoni diverter valve closes the diverter section when the tap goes off and takes the pump out of circuit from the PHE.
Simply leaving it running during the CH anti cycle time cannot clear this hot system water from the PHE
That doesn't sound right to me. The blue text - when the diverter closes, it's closed to the PHE. The open route is through the CH circuit.
So when the tap's turned off, the boiler water in the PHE just sits there. All of its heat would go into the DHW that's sitting in there, so that would heat up a bit more, but then it would be cooling down with time.
So after a CH period, overrun or no overrun, there shouldn't be any hot primary water in the PHE, unless as I suggested way back, the diverter is "letting by". In that case the stationary tap water sitting in the PHE would get up to the 80 odd of the CH water. So when the tap's opened, you get scalded.
The red text - other way round you might say - the PHE is taken out of the live pump circuit. The pump circuit carries on - through the CH.
Getting another pic together....
One of the green pipes comes from the Diverter (Orangey). I think it's the one on the left, the lighter one.
If the hot tap hasn't been used for a while, that pipe, and the whole of the DHW heat exchanger, should be COOL.
I bet it isn't, because the DV is letting water through, because of dirt in the system.