boilermate ov a class / glow worm hxi overheat

The GW and most modern boilers have a low water content and lightweight metal HE so they can overheat within 10 secs.

The c.i. suprima can probably manage this without any problem.

Have you seen if there is also a 15 sec delay before the pump starts when its controlled by your store?

Tony
 
Sponsored Links
as tony says it would be interesting to see if your one has a delay gas4you.

its unlikely i am going to see a BM a-class in the field. wouldve liked a fiddle with it to see what its like on a known working system
 