Hi Guys,
I have read through the 16thEd onsite guide (Fun not) to see if a ring main can be run horizontally around the room? and all it says on P53 is(no protection required) for Horizontally, vertically to an accessory box or within 150mm from angle formed by two walls or ceiling.
Does this mean that a cable can be routed from D/socket to the next D/Socket at 450mm from floor height or not?
I have not found anywhere that says you cannot? Or is it just (good practice) to run the cables up vertically from the first floor joists?
The walls are currently blockwork and brick and first-fix plumbing is done.
Cheers,
JC
I have read through the 16thEd onsite guide (Fun not) to see if a ring main can be run horizontally around the room? and all it says on P53 is(no protection required) for Horizontally, vertically to an accessory box or within 150mm from angle formed by two walls or ceiling.
Does this mean that a cable can be routed from D/socket to the next D/Socket at 450mm from floor height or not?
I have not found anywhere that says you cannot? Or is it just (good practice) to run the cables up vertically from the first floor joists?
The walls are currently blockwork and brick and first-fix plumbing is done.
Cheers,
JC