Extending ring main and lighting in to new extension
Would anyone use a 2.5mm² ring for a 32A cooker circuit? No, of course not.
And why not?
Many on here keep stating a 4mm² spur is suitable to take the full 32A load... What's the difference?
How about a parrallel fed 2x 2.5mm² for a 32A cooker circuit?
EDIT; Too slow.:(
And why not?
You tell me - if you have never done it.
My answer would be there is no point.
Using cables that have a CCC less than the rating of the OPD is not necessary.
There are regulations governing cables in parallel.
There is no point doing it if not necessary.
I have most certainly loaded 2.5mm² ring circuits right up to the 32A limit at a single point. It's a very common occurance in public entertainment. In fact I'll go further and claim to have fully loaded 40A 2.5mm² ring circuits at a single point.
That wasn't relevant to the question, however 'no point' is not a reason not to do it.
I have known it in new build where first fix cocked up.
Again not relevant to the question, however it is in the regs as a suitable design.
There are and I have conformed to those regs on a fairly regular basis. The regs are very handy.
Is doesn't have to be necessary to be a good way of doing it.
Ok. You win. I can't compete with that.
I know it's way outside of DIY/domestic etc but I've lost count of the times I've bunched multiple cables to get a temporary feed for stage lighting, heating, etc.
That's nothing to do with what was being discussed.
Do we any longer need a special category of circuit so we can use a 27A cable with a 32A OPD?
Actually, as you well know, the stipulation is a 20A cable but you mustn't use that one; instead use the next size up.
I do realise that it could hardly be banned because obviously it is safe - but is there really any point?
Or to put it another way if you really like rings, why is only the one configuration of ring circuit allowed?
Why not a 4mm² ring with 63A OPD?
We clearly don't 'need' it - i.e. we could certainly manage without it.
Quite so- and I don't think anyone has ever come up with a reasonable theory as to why we "mustn't use it".,
Good question. There are probably some circuit layouts which enable a ring to be installed which uses a little less copper than would radials(s). In comparison with 20A radials, it will usually mean half as many OPDs. Then, as I wrote earlier, it does provide 'CPC redundancy'. However, as I also said, there are also downsides.
Or to put it another way if you really like rings, why is only the one configuration of ring circuit allowed? Why not a 4mm² ring with 63A OPD?
To be the same 'ratio' (OPD/CCC = 32/20) as with a 20A CCC cable, it would presumably have to be no greater than a 50A OPD [ 37 x (32/20) = 59.2 ] (or maybe lower if, as to mirror the situation with 2.5mm², a CCC <32A were allowed) but, yes, that would seem logically consistent.
Given that ring finals were (I presume) introduced primarily with domestic installations in mind, I would imagine that (certainly then, and probably still now), if it ever were considered, it could well have been decided that there would be little call for a 50A sockets circuit in a domestic installation?
Kind Regards, John
Edit: numerical errors corrected
To be the same 'ratio' (OPD/CCC = 32/20) as with a 20A CCC cable, it would presumably have to be o greater than a 50A OPD [ 32 x (32/20) = 51.6 ]
Shouldn't you be using 37A - CCC of 4mm².
That still doesn't result in 63A, though.
I thought the criterion was 60% of the OPD rating.
32 x 0.6 = 19.2A
63 x 0.6 = 37.8A - albeit just over but I was just making the point.
There is also the fact that 2.5mm² rings could have a 40A MCB - 40 x 0.6 = 24A
Who says only one format is permitted, the regs list only one but that doesn't mean others are forbidden.
Biggest I've worked on was 120mm² 4C SWA on 300A fuses.
Kind Regards, John
Actually we inherited them from the maritime environment.
My understanding is that the standard 32A ring with cable that has a current rating of at least 20 amps and a size of at least 2.5mm² (1.5mm²) is "deemed to" comply with the requirements for overcurrent protection.
I would assume that for any other ring you would have to justify the incomplete overcurrent protection some other way.