I should have - I obviously has "32" stuck in my mind, hence the error. However, as you go on to say, that error doesnt aler my conclusion ...Shouldn't you be using 37A - CCC of 4mm².
... since, as you've obviously worked out, even 37 x (32/20) is, at 59.2, still less than 63. Now corrected - thanks for noticing!That still doesn't result in 63A, though.
Give or take some slight 'approximations' in your method (which resulted in 19.2A, rather than 20A), the things we are saying are mathematically equivalent.I thought the criterion was 60% of the OPD rating.
32 x 0.6 = 19.2A
63 x 0.6 = 37.8A - albeit just over but I was just making the point.
The 'ratio' of 32/30 (OPD/CCC), which is obviously using the precise 'reg figures' is simply the reciprocal of saying that the CCC has to be 62.5% of the OPD rating (whereas your "60%" only gave approximately the reg's min CCC figure).
If one applies that 62.5% to a 63A OPD, one gets 39.375A for the min CCC.
Indeed, and it still would if one used 0.625 (giving 25A) - but the reg is obviously clear in being specific to a 30/32A OPD, not specifying CCC as a percentage of any OPD's rating..There is also the fact that 2.5mm² rings could have a 40A MCB - 40 x 0.6 = 24A
Kind Regards, John