In theory the same risk applies for every socket in the circuit as applies to every junction box in the circuit. ~~~~~~ I've asked a question about voltage drop calculations for junction boxes. Is there something I need to factor in here?
A voltage drop in a junction box means heat is being created in the junction box. Voltage drop times current flowing gives the wattage of heat to be dissipated from the junction box.
No matter how much care is taken when screwing wires into junction boxes over time the copper deforms and the pressure from the screw onto the copper reduces. The resistance and volt drop increases. An out of sight ( but accessible ) junction box could get quite warm when this happens. You won't be aware unless you routinely inspect the junction boxes until the box fails completely. This will either mean loss of power to sockets ( but not on a ring final ) or a smell of burning. If the JB is in the loft you may not even smell it.
If a connection fails in a socket then the over heating and loss ( possible intermittent ) of power is immediately noticeable.
I am not a professional electrician, I am a DIYer but that is no reason that I would consider doing electrical work that did not meet professional standards as well as the standards of safety.