Radial circuit in a kitchen, 2.5 mm. cabel, two existing double sockets. Need to add two fused spurs and two more double sockets. Is this legal ? If it is not, what should I do?
Thanks
what breaker?
are those the only sockets in the kitchen?
what will those sockets by supplying?
the main reason to be carefull with 20A (which is the most you are allowed on 2.5mm radials) radials and kitchens is that if you put too much of the kitchen on them they will start tripping frequently