Emergency switching should "interrupt" the appropriate supply (537.4.1.3) So if the supply is via a contactor the coil circuit must be "interrupted" i.e. N/c.That is incorrect, data centre epo's normally operate via n/o contacts, the circuits are fault monitored and sometimes duplicated. The logic is to avoid the risk of a break in the circuit causing an expensive shutdown. Therefore any control circuits that could effect IT operations should be in a quiescent (de-energised) state.
I hope we're not getting confused between a single point of shutdown for whatever reason and emergency switching.