Ventilation to a gas fire with central heating back boiler

Discussion in 'Plumbing and Central Heating' started by John.Perham, 8 Nov 2005.

  1. John.Perham

    Joined:
    8 Nov 2005
    Messages:
    1
    Thanks Received:
    0
    Location:
    West Midlands
    Country:
    United Kingdom
    I have just been loooking at a house for a daughter and the living room has a New World Stowaway 411 gas fire in the fireplace with a back boiler and connected to the chimney which has a traditional clay pot on the chimney stack. There is no additional ventilation to the room as I was expecting. Should there be? Comments appreciated.
     
  2. ollski

    Joined:
    8 Oct 2003
    Messages:
    4,981
    Thanks Received:
    72
    Location:
    Birmingham
    Country:
    United Kingdom
    Yes there should be a terminal and 65cm2 ventilation direct to outside, ducted, no fly screen etc. This boiler is going to be 35 years old....treat it as needing urgent replacement.
     
  3. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,373
    Thanks Received:
    3,638
    Location:
    London
    Country:
    United Kingdom
    It should certainly have the ventilation into the room and could be considered as At Risk without it.

    As to the flue terminal, it is quite possible that when it was originally installed, the pot was acceptable in which case it would be classed as Not to Current Standards.

    More interesting perhaps is whether it has a flue liner which seems unlikely if there is no terminal.

    If there is no flue liner then the question arises, should it have one?

    Most professionals are wary of back boilers because so many safety issues arise. I dont remember ever seeing one without a flue liner although there may have been some early models which did not not need them.

    Tony
     
  4. ollski

    Joined:
    8 Oct 2003
    Messages:
    4,981
    Thanks Received:
    72
    Location:
    Birmingham
    Country:
    United Kingdom
    Tony no ventilation is at risk full stop, in fact anything under 40% is currently at risk. The instructions for this model state it must be on flue lined chimney and must have a British Gas approved flue terminal.
     
  5. Paul Barker

    Joined:
    4 Aug 2005
    Messages:
    9,626
    Thanks Received:
    867
    Location:
    Yorkshire
    Country:
    United Kingdom
    25 quid for a 5" tubulavent, 100 quid for flexible flue liner complete with correct terminal. 10 quid for firestop register/plate. Necessary documentation and noitce plate, half a days pay and your legal again.
     
  6. ollski

    Joined:
    8 Oct 2003
    Messages:
    4,981
    Thanks Received:
    72
    Location:
    Birmingham
    Country:
    United Kingdom
    The stowaway 411 ceased production in 1972, now I'm all for 'if it ain't broke don't fix it', but that is just throwing good money after bad. Would you want your daughter to live with it :confused:
     
  7. PEDANTICVINDICTIVEMAN

    Joined:
    10 Jul 2004
    Messages:
    7,191
    Thanks Received:
    1,285
    Country:
    United Kingdom
    Scrap it and put a steamer in, the most I would do is fit ventilation, anything else is a waste of money, if it packs up two weeks later where you gonna get he spares.
     