PostPosted: Fri Mar 16, 2012 10:10 am Reply with quote

My tenant actually told me that the BG engineer didn't try anything or switch anything on.

Anyway, after extensive testing we've figured the problem out. The cable going from the ceiling switch does not go directly to the shower. The cable is actually 10 sq mm cross section and fine.

For some reason only known to the people who put the extention on the flat back in the 70's, there is some sort of junction between the shower cable and the ceiling switch cable.

It's the junction that is causing the intermittent fault. When we tested the cable going to the shower it was ocasionally showing a short. I have professionals coming to remedy the problem this morning.

Of course none of this would be solved by the BG engineers solution of replacing the fusebox.

One question I have though - is the Wylex 16th edition fusebox not up to current standards for residential or use by tennants? Do I legally have to get this replaced? Or is the BG engineer talking rubbish?

Dan
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Fri Mar 16, 2012 10:26 am Reply with quote

..


Last edited by holmslaw on Thu Apr 12, 2012 8:18 am, edited 1 time in total
Back to top
 Alert Moderators
otisthecat

from United Kingdom

Joined: 13 Mar 2012
Posts: 6
Location: Newcastle upon Tyne,
United Kingdom

PostPosted: Fri Mar 16, 2012 12:25 pm Reply with quote

I have a gas and electricity inspection carried out every year as I'm supposed to. This is why I was suprised at the BG engineers comment.

I did think that these regulations are not retrospective, but I now have to reassure my tennant after the BG engineer has him convinced otherwise.

Thanks

Dan
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 11842
Location: Oxfordshire,
United Kingdom
Thanked: 929 times

PostPosted: Fri Mar 16, 2012 2:36 pm Reply with quote

otisthecat wrote:
I have a gas and electricity inspection carried out every year as I'm supposed to.


You might like to consider the value of that if that is being done by BG.

BTW You don't need an annual electrical inspection of the installation. Portable Appliances, maybe, but no the installation itsellf.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page Previous  1, 2
Page 2 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Triton Spellbind shower tripping RCD 71 7540 Sat Mar 15, 2008 12:52 pm
Shower keeps tripping out - 4 weeks after fitting! 3 560 Wed Sep 03, 2008 8:15 am
Shower tripping main fuse 6 160 Sun Aug 25, 2013 5:57 pm
new shower-tripping rcd 6 420 Mon Sep 19, 2005 9:09 pm
Electric shower tripping rcd/mcb 34 340 Sat Jul 27, 2013 9:03 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.