Ventilation to a gas fire with central heating back boiler


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
John.Perham

from United Kingdom

Joined: 08 Nov 2005
Posts: 1
Location: West Midlands,
United Kingdom

PostPosted: Tue Nov 08, 2005 4:17 pm Reply with quote

I have just been loooking at a house for a daughter and the living room has a New World Stowaway 411 gas fire in the fireplace with a back boiler and connected to the chimney which has a traditional clay pot on the chimney stack. There is no additional ventilation to the room as I was expecting. Should there be? Comments appreciated.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Tue Nov 08, 2005 5:54 pm Reply with quote

Yes there should be a terminal and 65cm2 ventilation direct to outside, ducted, no fly screen etc. This boiler is going to be 35 years old....treat it as needing urgent replacement.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52153
Location: London,
United Kingdom
Thanked: 3251 times

PostPosted: Wed Nov 09, 2005 11:15 am Reply with quote

It should certainly have the ventilation into the room and could be considered as At Risk without it.

As to the flue terminal, it is quite possible that when it was originally installed, the pot was acceptable in which case it would be classed as Not to Current Standards.

More interesting perhaps is whether it has a flue liner which seems unlikely if there is no terminal.

If there is no flue liner then the question arises, should it have one?

Most professionals are wary of back boilers because so many safety issues arise. I dont remember ever seeing one without a flue liner although there may have been some early models which did not not need them.

Tony
Back to top
 Alert Moderators
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Wed Nov 09, 2005 3:34 pm Reply with quote

Tony no ventilation is at risk full stop, in fact anything under 40% is currently at risk. The instructions for this model state it must be on flue lined chimney and must have a British Gas approved flue terminal.
Back to top
 Alert Moderators
Paul Barker

from United Kingdom

Joined: 04 Aug 2005
Posts: 9118
Location: Yorkshire,
United Kingdom
Thanked: 703 times

PostPosted: Wed Nov 09, 2005 6:34 pm Reply with quote

25 quid for a 5" tubulavent, 100 quid for flexible flue liner complete with correct terminal. 10 quid for firestop register/plate. Necessary documentation and noitce plate, half a days pay and your legal again.
Back to top
 Alert Moderators
ollski

from United Kingdom

Joined: 08 Oct 2003
Posts: 4906
Location: Birmingham,
United Kingdom
Thanked: 55 times

PostPosted: Wed Nov 09, 2005 7:04 pm Reply with quote

Paul Barker wrote:
25 quid for a 5" tubulavent, 100 quid for flexible flue liner complete with correct terminal. 10 quid for firestop register/plate. Necessary documentation and noitce plate, half a days pay and your legal again.


The stowaway 411 ceased production in 1972, now I'm all for 'if it ain't broke don't fix it', but that is just throwing good money after bad. Would you want your daughter to live with it icon_confused.gif
Back to top
 Alert Moderators
PEDANTICVINDICTIVEMAN

from Western Sahara

Joined: 10 Jul 2004
Posts: 6569
Location: Western Sahara
Thanked: 1028 times

PostPosted: Wed Nov 09, 2005 7:36 pm Reply with quote

Scrap it and put a steamer in, the most I would do is fit ventilation, anything else is a waste of money, if it packs up two weeks later where you gonna get he spares.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Back boiler ventilation !! 11 1580 Wed Aug 05, 2009 9:43 pm
Back boiler 'At Risk' ventilation problem 26 2120 Thu Jun 11, 2009 1:26 pm
Trianco 25/40 Back boiler - Ventilation?? 5 820 Sat Apr 26, 2008 12:03 pm
Back boiler ventilation 3 80 Tue Jun 12, 2012 1:13 pm
Ventilation for a back boiler 11 900 Sat Dec 20, 2008 2:54 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.