A little Help OFTEC Engineers
9 Oct 2009
Shropshire
Hello all
Just got back from an oil boiler serviced 2 weeks ago customer complained burning sooty went back changed nozzle did another analysis 12% co2 the sooty exhaust gone but the only thing that concerns me is the flue exhaust temp got up to 400 C is this the soot burning off ? The manual says flue temp 240 C Why is it soo high any help thx..
Did you clean the boiler out after the sooty episode?
And are all the baffles in correctly, and in an undamaged condition?
Is the heat exchanger vented of air?
Basically the heat generated by the burner isn't being dissipated into the walls of the main burner chamber and through the baffles efficiently enough. As Simond has said, check that everything is in the correct position, and not missing. What make is the boiler / burner? See if you can download info on it, to see if anything was missing or not installed correctly :)