Shower circuit confusion !
26 Nov 2010
Birmingham
hello again ,
some advice needed please ? Im currently studying towards my full scope domestic electrical installer qualification. My confusion starts with my shower circuit at home , i currently have a 9.5kw instantaneous shower fitted with 10mm cable back to a 32A MCB. Is this correct because through my calculations and with reference to BS:7671 it doesn't seem to add up ?
With reference to the BS:7671 OSG cable selection theory it points me towards:
9.5KW/230V=(lb)41.3A so in order for : ln>lb it would need to
be a 50A MCB?
I apologise if im being thick but if so could somebody set me straight , thanks for your time !!!!!!
hello again ,
be a 50A MCB?
9500 W / 240V = 39.58 A
If you run it on 230V it will consume less power and take less current because the voltage is lower, the resistance remains the same.
If it's a new shower it might actually be rated at 230V, but an older one will be rated at 240V.
be a 50A MCB?
45 Amp should be enough if your consumer unit manufacturer makes it.
9500/240 = 39.6A
9500/230 = 41.3A
How does that work then? It will pull a higher current at a lower voltage.
[9500/240 = 39.6A
9500/230 = 41.3A
BS7671 17th Edition uses 230v as the standard throughout.
Shower manufacturers in particular promote the headline figure of say 9.5kw shower @ 240 volts.
which equates to 8.7kw @230v
9500/240 = 39.6A
9500/230 = 41.3A
By what magic will the resistance of the heating element drop from 6.06Ω to 5.57Ω when the voltage reduces?