That's not what it says.537.2.1.3 applies to any situation where the actual live 'parts' can be re-energised from more than another supply.
It's not the DB which has dual supplies, it's the light switch.This situation will never arise with a multi gang light switch. Because to isolate a switch you identify the circuit at the db and pull the fuse. So even if the db has dual supplies, you're still completely safe because you have isolated the individual circuit.
537.2.1.3 requires a warning notice because the live parts inside the switch enclosure cannot be isolated from a single point.
Where an installation, item of equipment or an enclosure contains live parts connected to more than one supply..."Thats why 537.2.1.3 does not apply, the teminals 'parts' maybe adjacent but they are different 'parts' individually supplied and/or isolated.
Do you not consider a switch to be an item of equipment?
Do you not consider the box it's mounted in to be an enclosure?
A multi-gang switch is one item.It is for the individual switches.
The box it is in is an enclosure.
If the circuits supplying the one item, or the enclosure, can't be isolated at a single point then 537.2.1.3 applies - it says so quite clearly.
I am asserting that in cases where more than one circuit is supplying the switch and they can't be isolated at a single point.If you're ascerting that multi gang switches need one point of isolation then take it up with the IET.
And I have no need to take it up with the IET, as what they say about it is unambiguous.
And ordinary switches have to be removed before you can test for dead.You could also point out non compliance with the EAWR, because you have to dismantle a grid modules before you can test for dead.
Equipment covers have to be removed before you can check for dead inside them.
Those are not contraventions of the EAWR.