Two Red Wires into Earth Terminal on back box (Two Gang)

Discussion in 'Electrics UK' started by ben123d, 7 Jan 2020.

  1. ben123d

    ben123d

    Joined:
    7 Jan 2020
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    I am changing a two gang light switch from a older plastic version to a metal one.

    Moving the earths from the back box to the earth terminal on the light switch / plate, but on the two gang on the landing there are two red wires going into the earth terminal in the back box.

    Do these get moved to the earth terminal on the light switch or remain where they are?
     
  2. Sponsored Links
  3. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    3,605
    Thanks Received:
    709
    Location:
    Durham
    Country:
    United Kingdom
    You may find that those 2 red cores are live and some lazy installer has used the terminal in the plastic box instead of going back to their van and getting a piece of choc block. Or I've misunderstood and the landing switch has a metal backbox?

    Before doing anything you should check that the CPCs (the bare conductors) or anything else you think is ground are actually connected to ground- with your old plastic switchgear lack of earth is not a problem, with your metal switch bad things could happen.

    EDIT Good practise to link from the earth terminal on the switch to the earth terminal on the backbox
     
    • Thanks Thanks x 1
  4. ben123d

    ben123d

    Joined:
    7 Jan 2020
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    It's a metal back box and metal switch. Just tested both wires with a multi meter and it's showing nothing for both. I assume they have just been 'parked' in the box terminal
     
  5. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    3,605
    Thanks Received:
    709
    Location:
    Durham
    Country:
    United Kingdom
    OK. So is there any other sort of earth wire at the landing switch?- if not, you can't use your new metal switch. Out of interest, what did you test the red wires against?
     
  6. ben123d

    ben123d

    Joined:
    7 Jan 2020
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    I tested against the back box. Got a reading off the live going into L1, but nothing off the two reds going into the earth terminal on the back box.

    Apologies, should have been clearer in the original post. There are two earths also going into the back box earth terminal.

    I have now sleeved both and put into the earth on the switch plate. I have a put a fly earth from switch plate to back box. I have left the two 'dead' red wires in the earth terminal on the back box.

    Just switch the lights back on at the consumer unit and tried the switch, no problems. I have also tried the downstairs switch controlling the same lights, no problems (i.e. I'm still alive and not tripping).
     
  7. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    34,672
    Thanks Received:
    3,849
    Location:
    Retired to:
    Country:
    Portugal
    Putting wires in an earth terminal is a way of terminating them safely and showing that they are unused and not live.

    Put them in the switch terminal with the earth wires.
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page