I fear that the situation is probably much more messy/confusing, with widespread misuse of terminoolgy, than you go on to suggest.For anyone who was as confused as me with the mixture of terminology in this thread:![]()
When one uses this method, whether one is measuring resistance or impedance depends primarily upon whether one's Tester uses AC or DC for the testing. I don't know about other makes, but Fluke MFTs like the one I have (e.g. 1653B/1654B) use AC (25V 128Hz) - hence, despite the fact that the documentation and labelling of the machines all talks in terms of 'resistance', I can but presume that what is actually being measured is impedance (or maybe I'm wrong, and it's somehow managing to extract the resistive component?).A rod install can be tested in two ways.
You can measure Ra (The resistance of the rod to earth) using an 'Earth Electrode Resistance Tester'.
This is a 'dead' test and is measured between the end of the (disconnected) earthing conductor/CPC, through the rod and then through 'earth' to the two 'additional' probes in the ground.,
This is resistance, (hence the 'R' in Ra), and is measured in ohms.
The same is true if one uses the 'transformer method' of measuring an earth rod. In that case one definitely uses AC and simply measures the AC voltage applied and AC current flowing (with no consideration of phase angles/'power factor' etc.) - so one is definitely measuring impedance - although that is, again, almost always called 'resistance'.
In any event, what actually matters is earth path impedance (not that it will usually differ significantly from resistance), since any fault currents it carries will necessarily be AC.
Indeed - and that certainly is impedance that is being measured, since the test voltage then necessarily comes from the AC supply.For The other method is the same as your normal Ze test.
Measured with an 'Earth Loop Impedance tester', this measures the 'Earth Fault Loop Impedance' (which includes the 'rod'), and gives an impedance measurement in ohms.