misprint?
Its been a long day..
Just looking up some figures and came across this sheet on the esc website. ... but do the BS1361/2 fuse ELI max figures for 13a and 15a seem odd ?. http://www.esc.org.uk/fileadmin/use...y/faqs/master_EARTHFAULTLOOPtable.pdf[/QUOTE]
Indeed so - the figures for 15A should obviously not be higher than those for 13A. I'd have to cogitate a bit more to work out which (if either) is correct (or maybe the two are transposed).
3.06 is right for the 13A, with the 0.8 factor.
I've worked it out at 2.94 for the 15A, but not sure if that's right.
Page 48, Table 41.2 BRB.
Now BS 88-3 fuse system C. (1361 withdrawn)
Page 55, Table 41.2 BGB.
and reconfigured at 5,16,20 & 32A.
The 5A has the same max.Zs. but the 20A lower than before
Page 48, Table 41.2 BRB. Now BS 88-3 fuse system C. (1361 withdrawn)
Page 55, Table 41.2 BGB. and reconfigured at 5,16,20 & 32A. The 5A has the same max.Zs. but the 20A lower than before
Thanks; I guess that explains why I couldn't find figures for BS 1361!! However, the Table linked from the OP has a column for 'BS 88-3 System C' as well as for BS 1361/1362', but the figures in those columns don't correspond - so do I take it that, whilst the former has 'replaced' BS 1361, they are not direct equivalents?
I hadn't noticed/looked at that. No 88-3 in BRB.
Except the 5A @ 0.4s ???
I would assume (never assume) so, hence my comment about the 20A.
As the 'new' ones have a slightly higher max.Zs I suppose they must be faster acting with a lower fusing factor and so 'better'.
Indeed, that is correct. 5A @ 0.4s is the same for both 'BS 1361/2' and 'BS 88-3 System C'.
Indeed, that would appear to be the implication. They're actually not a lot 'worse' than a Type B MCB.