Assuming you mean Main Protective Bonding conductor - I would say YesIs it OK to use 2 x 6mm cables in parallel in place of 1 x 10mm.
TIA
Not really. Your thinking of Supplementary Bonding.But is the idea not to keep the touch voltage down to less than 50V
I don't know what you mean.and not blow a 100A fuse?
No, it's not a reg.0.05Ω max cannot be a reg.
That clearly should be the case, but is there not a problem in calculating the required MPB conductor CSA unless one knows the resistance to earth from the (bonded) extraneous-c-p? Do you simply consider the 'worst possible scenario'? I would imagine that such a 'worst possible scenario' would have to assume total loss of the installation's earth combined with a negligible impedance L-MET/CPC fault in the installation (at a point where it was only protected by the service fuse), with an assumed resistance from extraneous-c-p to earth of zero. In that situation, I presume that the potential fault current would presumably approach double the PSCC. Is that how you would do it?Main Bonding is sized to be able to carry, without damage, the currents caused by a fault to earth or a fault on the network.But is the idea not to keep the touch voltage down to less than 50V
I'm sure you knowThat clearly should be the case, but is there not a problem in calculating the required MPB conductor CSA unless one knows the resistance to earth from the (bonded) extraneous-c-p?Main Bonding is sized to be able to carry, without damage, the currents caused by a fault to earth or a fault on the network.But is the idea not to keep the touch voltage down to less than 50V
No, not specifically.Do you simply consider the 'worst possible scenario'?
I suppose it would be but is that possible, not to mention likely?I would imagine that such a 'worst possible scenario' would have to assume total loss of the installation's earth combined with a negligible impedance L-MET/CPC fault in the installation (at a point where it was only protected by the service fuse), with an assumed resistance from extraneous-c-p to earth of zero.
You mean - double because of the e-c-p to earth of zeroΩ?In that situation, I presume that the potential fault current would presumably approach double the PSCC.
Is it really as simple as that? I would have thought that 'PEFC' is, in itself, not directly relevant to the current which could flow along an MPB conductor, since it is determined on the basis of fault current flowing through the installation's 'normal' earth connection. The calculation you describe would be appropriate for the installation's main earthing conductor (from MET to earth) but does not directly tell us what could flow through the bonding conductor (particularly if the main earth was 'lost') - that will depend upon the 'Ze' of the extraneous-c-p, not of the normal earthing arrangement. Also, when you talk of 'PEFC' do you mean with or without MPB connected?I'm sure you knowbut - We only have to calculate from the (actual) PEFC or fit the stated csa.
Incredibly unlikely, I would say, but I'm not clear how unlikely a (theoretically) 'possible' scenario we have to design for. Quite frankly, I would suggest that it's probably also incredibly unlikely that one would ever see a current in an MPB conductor which couldn't safely be carried by a 2.5mm² or smaller conductor - but we are clearly expected to design for worse scenarios than that.I would imagine that such a 'worst possible scenario' would have to assume ... I suppose it would be but is that possible, not to mention likely? A fault from L tail to MET/CPC within CU while EC disconnected AND zeroΩ to earth via e-c-p. (Who have you been talking to?)
Yep, a return path of zero impedance, rather than (per PSCC) the impedance of the N conductor back to the transformer.You mean - double because of the e-c-p to earth of zeroΩ?In that situation, I presume that the potential fault current would presumably approach double the PSCC.
Sort-of - but if one is not going to assume the worst (obviously impossible) case of a zero 'Ze' for the extraneous-c-p, what alternative figure do you think we should assume?In other words a 'perfect TT'.
I'm not sure I understand that - maybe I'm missing something.Of course, with such a fault the bonding conductor would not have to be very big, would it? A lesser and even more unlikely fault would need to occur to cause it damage.
Consider (easy numbers for illustraton) ... PSCC = 920A, hence impedance of supply L = impedance of supply N = 0.125Ω. MPB conductor 0.05Ω, assumed 'Ze' of extraneous CP zero. Real earth 'lost'. Negligible impedance L-CPC/MET fault. Current in MPB conductor = 230/(0.125+0.05) = 1314A. Would a 'not very big' conductor suffice?
Even if, more realistically, one assumed that the 'Ze' of the extraneous-c-p were 0.25Ω (which is what my water supply pipe IS), the MPB current would be 230/(0.125+0.05+0.25) = 541A, which might still not do too well with a 'not very big' MPB conductor.
Am I missing something?
Yes.Is it really as simple as that?We only have to calculate from the (actual) PEFC or fit the stated csa.
It may not be but the EC csa is calculated from the PEFC (without bonding) and the MEB is half of that or as stated for PME.I would have thought that 'PEFC' is, in itself, not directly relevant to the current which could flow along an MPB conductor,
It is half of that calculation except PME.since it is determined on the basis of fault current flowing through the installation's 'normal' earth connection. The calculation you describe would be appropriate for the installation's main earthing conductor (from MET to earth)
As above - without.but does not directly tell us what could flow through the bonding conductor (particularly if the main earth was 'lost') - that will depend upon the 'Ze' of the extraneous-c-p, not of the normal earthing arrangement. Also, when you talk of 'PEFC' do you mean with or without MPB connected?
I don't see how that can happen so I suppose the PEFC is adequate for use.Yep, a return path of zero impedance, rather than (per PSCC) the impedance of the N conductor back to the transformer...
... but if one is not going to assume the worst (obviously impossible) case of a zero 'Ze' for the extraneous-c-p, what alternative figure do you think we should assume?
As above, but I'm surprised that you are asking these questions.I'm not trying to be awkward, nor even am I playing Devil's Advocate. I'm genuinely trying to understand the basis on which one is meant to calculate the required CSA for a MPB conductor (if one choses not to use the 'default' {'stated'} CSA), and the reasoning behind that basis.
Yes, that's how it's done.Are you saying that you would calculate it on the basis of the PEFC - i.e. the L-E fault current that would flow through the 'real earth' (if intact) in the absence of any bonding?
With TT obviously, TN-S is usually comparable with TNC-S as far as Ze goes.Do you not entertain the possibility that certainly with TN-S, and obviously with TT) that the extraneous-c-p could have a lower resistance to earth than the installation's 'earth', such that higher currents than the 'PEFC' might flow in the MPB conductor?