Easy Discrimination Quiz
27 Mar 2007
Surrey
We all love a bit of discrimination, so as a result of the cliche hedge-trimmer-cut-through-flex accident that befell me last weekend, which device or devices operated?
Flex was two-core.
In order from appliance:
1. Appliance plug 5 A fuse
2. 13 A fuse in switched FCU for outside socket
3. 20 A MCB
4. 80 A / 30 mA RCD
5. DNO fuse
Winner gets to feel briefly smug.
My guess is 3.
4 probably wouldnt have tripped as it was a direct short between live and neutral.
MCB probably acts quicker than the two wire fuses in a dead short situation.
I don't know, but in my wire-cutters-through-T&E the other week the only thing that blew were the wirecutters.
1 & 3 & 4
Cut lead fell to the ground and caused an imbalance to earth when landed in a puddle.... :)
I'll give it another 15 mins. And to add to the excitement, the winner will get a dedicated favourite quote from b-a-s.
Well, I did a similar thing with a lawnmower years ago.'82 I think.
The 1362 definitely did not pop and neither did the RCD. Until I picked up the lead end (silly sod).......
The breaker will fail in preference to the 13A 1362, so I reckon it's down to either the breaker or the DNO's fuse.
Now, if the DNO's fuse is a 3036, then the breaker will pop first.
But if the DNO fuse is an 88/3 or weak, who knows?
I'll go with the DNO fuse.
When I did it (identically, with a Class II hedge cutter) two or three years ago, the fuse in the plug and the local 20A MCB did not operate, but the 60A 1361 fuse protecting the sub-main concerned popped! (and the RCD did not operate)
Well Iggifier is the winner with:
1. (5A plug fuse); and
3. 20 A MCB
And the pearl of b-a-s's wisdom is:
"They are useless at lighting up any room, because, more than just not being designed to do that, they are actively, positively designed to not do it."