An extract form BS 6400-1 which actually tells you how to calculate the actual load
Annex A (normative) Sizing of meters
A.1 Diversity factor
A diversity factor is given to each type of appliance according to the normal degree of intermittence of use. Where there is only one or two appliances (e.g. combination boiler and cooker) the diversity factor shall have a value of one. Where there are more than two appliances the diversity factors listed in Table A.1 shall be used.
A.2 Meter size calculation
To calculate the size of meter required, multiply the maximum heat input of each appliance by its diversity factor, add these figures, convert to megajoules, and divide the total by the calorific value of the gas (typically 39 MJ/m3 for 2nd family gas). The following is an example of such a calculation.
Table A.1
Diversity factors of appliances for meter sizing
Appliance Diversity factor
Central heating appliances (other than combination boilers) 1.
Unit heaters 1.
Circulators 1.
Combination boilers 0.8.
Instantaneous water heaters 0.8.
Sink water heaters 0.6.
Room heaters 0.6.
Tumble dryers 0.6.
Hotplates 0.6.
Ovens 0.6.
Cookers 0.4.
Refrigerators 0
We need to know the maximum gas flow rate of the installation. This can be calculated by using the makers stated GROSS heat input. Where the makers state a NET figure we have to multiply this by 1.11 (Natural Gas)
As it is unlikely that all appliances will be on full load at any one time, a diversity factor is applied where there is more than two appliances depending on each appliances level of use. Where there is only one or two appliances installed no diversity factor is applied with the gas consumption calculated on the total heat input of the installation. If only two combis are fitted then a diversity factor is not needed to be calculated.
e.g.:
- 1st Combi 30kW gross x 0.8 = 24.
- 2nd Combi 30kW gross x 0.8 = 24.
- hob 9kw gross x 0.6 = 5.4
Total = 53.4 kw
53.4 x 3.6 = 192.24 Divided by CV of 38.76 MJ/m3 =
4.960 cu m/hr. If the appliance figures above are GROSS.
If the appliance figures above are NET then multiply by 1.11 = 4.960 x 1.11 =
5.51 cu m/hr. Well within a U6 meter's capacity with lots to spare. The meter has an overload and can pass more than 6 cu mtrs/hr. The diversity factor allows the stated limit of the meter to be exceeded, but on an intermittent not permanent basis. A U6 meter has an overload of 100%.
Such fun. The OP can cheaply and easily install an additional combi and even have a hob.