Radiator sizing
23 Feb 2016
I'm about to start fitting the first of some new radiators, i think i get most of it.
So far i have used this calculator. http://www.theradiatorcompany.co.uk/heatoutput/
4.140 x 2.970 x 2.440 with a large window.
This gives me an upper figure of 5275 BTU (1546kw) for the room in question. Now i understand this is based on a delta t50, but with wanting a combi it would most likely be around t40, or even 30 if i can run the boiler that way, aim for a 20c drop in temp. 70/50/20, or 60/40/20 if it will go that low.
What calculation do i need to convert to different delta t?
This should help.
To apply the factors shown in the table below to the quoted outputs, multiply the quoted output by the chosen operating factor to give new output. E.g a nominal 1kw radiator with a ΔT of 40C will produce 1000 x 0.748 =748W.
To apply the factor to required output, divide required output by factor to give correct radiator size. e.g to produce 1kW with a ΔT of 40C you will have to install a 1000 ÷ 0.748 = 1337W radiator, or the nearest larger.
ΔT is the difference between mean water temperature and room temperature in °C The table shows the factors for ΔT other than 50°C.
ΔT - Factor
10 - 0.057
10 - 0.123
15 - 0.209
20 - 0.304
25 - 0.406
30 - 0.515
35 - 0.629
40 - 0.748
45 - 0.872
50 - 1.000
55 - 1.132
60 - 1.267
65 - 1.406
70 - 1.549
75 - 1.694
Great just what i was after, looks like the room needs around 3kw at delta t30 or 2kw at 40. Makes a big difference.
Looks like the room needs around 3kw at delta t30 or 2kw at 40. Makes a big difference.
Not strictly correct. The room needs 1546W (not 1546kW as in your opening post!!). But you will have to install a rad with a nominal output of 2kW or 3kW, depending on ΔT, to achieve the required output.