Ravenheat 820/20T
13 Apr 2009
Northamptonshire
Ravenheat 820/20T .....been reliable over the years.....the problem I have and I hope you can shed some light on why there's no hot water at the tap(?)....The central heating is working perfectly but for some reason there's no hot water.
I see thermistor gets mentioned a lot for this type of problem but I don't think the 820/20T is fitted with one - is that correct?
Many thanks.
The boiler has a thermistor but not likely to be your problem.
You need to check the diverter valve is moving and operating the DHW demand switches!
Tony
That's very true - I think I'll have an engineer install a new diverter valve(with micro-switch) and cross my fingers......many thanks for your assistance, Tony......
why ? just get an engineer out to diagnose the fault rather than say it needs a diverter valve and micro-switch, most probably the DHW Diaphragm has perished on your boiler
It is a scraping knuckles boiler.
But I do just replace the diaphragm on that model!
Tony
It doesn't. It's a thermostat which switches a high and low gas rate at the gas valve (not fully modulating).
Lad, your post count is not even 3k. You need high 60k to carefully and precisely state a thermistor is same as a thermostat. you are not implying these components are different are you?
I am still trying to get to grips with capacitors and ECR meters. I think you need to get to grips with thermistors and thermostats- you will eventually realise there is no difference, once you get an oscilloscope(y)
Yes, that is correct, its such an old design that it uses a phial type thermostat to give three different contact outputs.
As it was not related to the fault on the OP's boiler, in my haste I wrongly said it was a thermistor!
I am still keeping one of this old model going until the summer when I will replace it with an Intergas.
  • Thanks
Reactions: DP