Hi all,I've obtained building regs to knock down a couple of load bearing walls architect and structual engineer involved,but with a caveat added that they want more info regarding load bearing A,I'll add the drawings to show what I have.
The council and the engineer seem to be at odds and I'm in the middle.
Any thoughts?
Steel beams supporting new external wall to kitchen—maximum span = 3.60m
Same Loadings:
Beam ‘A’ - Section size: 2No. 203x133x30 UB Grade 43 – Maximum span 3.60m PL and UDL Load D= 206.8mm B=133.9mm t=6.4mm T=9.6mm Ix=2,900cm4 ry=3.17cm Zx=280cm3 Le/ry = 3.20x100.00/3.17 = 123 D/T = 21.50
Permissible bending stress pbc = 138.5N/mm2 (Table 3a) Actual bending stress fbc = 30.15 x 1000/280.0 = 107.7N/mm2 Therefore OK.
Maximum shear = 24.50x1000/(6.4x206.8) = 18.52N/mm2 Therefore OK.
Check unstiffened web capacity with load of 34.15 Bearing Pb = 210N/mm2 (Table 9) C1 = 40.0KN; C2 = 1.34KN/mm Buckling Pc – 146N/mm2 (Table 17a) C1 = 96.6KN; C2 = 0.934kN/mm R1 unstiffened web capacity, Pw = 33.2KN – no stiffening required R2 unstiffened web capacity, Pw = 33.2KN – no stiffening required
Total deflection = 28.3x1e8/205,000x2,900 = 4.8mm (L/631) Therefore OK.
Combined bearing and shear check (14.c): (fbc/ pbc) 2 + (fs/ps)2 = 0.605 at 2.00m Less than 1.25 = Therefore OK
Bearing details: 100mm end bearing with steels built into blockwork at both ends R1 (17.50KN unfactored): 15mm mild steel bearing plate, size 250x100mm = 1.18N/mm2
Steelwork bearing to garage – 600mmx100mmx420mm C30 concrete padstone
Beams to be bolted together ay 600mm centres
Beam ’B’ into garage—Section size: 2No. 178x102x19 UB grade 43 – Maximum span of 2.2m Maximum bending moment = 1.10metres from R1 Maximum SF = 33.39 at R1 Total deflection = 14.8x1e8/EI at 1.10 from R1 (E in N/mm2, 1 in cm4)
Steel calculation to BS449 Part 2 using S275 (Grade 43) steel UDL Loading only D= 177.8mm B=101.2mm t=4.8mm T=7.9mm Ix=1356cm4 ry=2.70cm Zx=153cm3 Le/ry = 3.40x100.00/2.70 = 126 D/T = 37.04 Permissible bending stress pbc = 130.1N/mm2 (Table 3a) Actual bending stress fbc = 10.49 x 1000/153.0 = 68.56/mm2 Therefore OK.
Maximum shear = 16.21x1000/(4.8x177.8) = 18.99N/mm2 Therefore OK.
R1 (17.50KN unfactored): 15mm ms bearing plate, size 250x100mm = 1.18N/mm2 R2 (17.50KN unfactored): Bolted to main steel above .
Any thoughts?
Same Loadings: