In the old days, all you wanted from a motorised valve was simple open/closed, however with the introduction of modulating boilers, I would expect you now need to control how much the valve is opened. The TRV with electronic head I hear the motor run from time to time as it adjusts how far open the valve is. I hear it run at 10 pm as the program calls for temperature to be reduced over night. I assume same goes for any zone valves.
No, zone valves tend to be either open or closed, as previously mentioned they were perhaps the first iteration of adding controls to an otherwise uncontrolled system. One house we used to live in was built in '69, oil boiler, and no controls other than a time clock. The design principle was that the boiler runs when the time clocks says so, once the system is hot it starts cycling, and by balancing the system you got the rooms to "reasonable" temperatures. Dad added a room stat as one of the first things he did, and the boiler engineer used to comment on how clean the boiler was inside - thanks to the lack of short cycling.
I looked at fitting all electronic TRV heads but it works out rather expensive.
Indeed, waiting to see what the next batch of OpenTRV (aka
Radbot) heads turn out like, supposedly due out around October - should cut the cost down significantly. But if you ignore the modulating for a moment, you can think of these as "a zone valve per radiator" - ie extending the idea of zones down to room level. As an aside, one of the other houses (actually a bungalow) in our new street was customer fitted for the purchaser - he had a wall stat and zone valve for each room which was "really cutting edge" for the early 70s.
TRVs, especially programmable electronic ones, take that one step further by modulating the radiators rather than just being on-off.
You can run the system with the boiler just "doing it's own thing", or it's better if the TRVs signal to the boiler when heat is actually needed - that's fairly easy to do just with a "radio controlled relay" that switches on the boiler when there's a TRV signalling for heat.
The big problem for all forms of TRV is that the flow requirements for the heating are incompatible with the flow requirements for the boiler - and boiler manufacturers seem to still have their heads stuck in the last century
Basically the flow requirements are for lower flow as demand reduces, but the boilers are designed for a minimum flow which usually means not far off a constant flow - hence the need for a bypass. But, this means that as load reduces, there needs to be more bypass, and the return temperature to the boiler increases. With a variable flow system, the return from the rads reduces with reducing demand.
When I get to that stage, I'll be fitting a thermal store in our house - decoupling the boiler from the heating (and hot water, I really don't like combi boilers
) which means the heating can use a modulating pump which I can tell you makes for a nice quiet system (non of the hissing so often found as the pressure goes up as the valves close off).
And an interesting arrangement of the plumbing (may need a separate FGHR unit) to maximise condensing in the boiler while satisfying the manufacturer's requirement for constant (excessive) flow.
At the moment only one fan assisted radiator is fitted, would like to fit more, specially in the kitchen, they had one huge difference to the non fan assisted, they don't hold much water, this means the circulating water can heat up, and cool down much faster, as there is less of it. So walk into cold house and within 5 minutes of the heating going on the Myson is kicking out hot air. However same in reverse, within minutes of the thermostat switching off the boiler the radiator is cold and the fan auto turns off,
Indeed, those fan coils are very effective at getting heat from the water to the air in a small space - and that's especially useful if you want to run a low temperature system to make best use of renewables (and a condensing boiler). I would be inclined to use a TRV to modulate the flow rather than an on-off stat - that would avoid the hot-cold-off-hot-cold-off-... cycling.
... after running for 2 hours 'stalled', the DC resistance had increased from 2.02kΩ to 2.44kΩ (hardly 8kΩ!) but, interestingly, the current remained stubbornly unchanged at 31mA and, even more interesting, the PF had crept down from 0.98+ to 0.87 (so true power consumed had fallen a bit, despite the unchanged current). After 15 mins cooling, the DC resistance was back to just over 2kΩ and on powering up again, we were back to 31mA and a PF of about 0.98.
I can't help thinking that the shaded pole is what's doing the bulk of the losses.