Exactly so why are people saying 6kw max on the mcb? Makes no sense right and I should be ok as 10mm wire and 40a mcb should be more than enough
In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts.I have a kiln, 7.6kw 230 volts
I make that 36.3A and 9.2kW as the resistance would remain at 6.97Ohms.If the supply voltage is the maximum 253 then the kiln will be taking 8.36 kW ( 7.6 / 230 ) x 253 which is 33 Amp.
Some people say the world is flat. I saw something on the internet once which was wrong.Exactly so why are people saying 6kw max on the mcb?
Yes, literally more than enough as in too big and a waste - unless you have installed it in unfavourable surroundings.and I should be ok as 10mm wire and 40a mcb should be more than enough
You did not go wrong. I went wrong. I left the square out of the formulaWhere am I going wrong?
I have some Memshield 2 MCBs and RCBOs, which fit.Is there perhaps some confusion with the 6kA breaking capacity of the OPDs in domestic CUs?
Yes this is the thing. I worked it all out upgrading from 6 to 10mm and a 40amp type b mcb. Then someone said the mcb has 6kw max. These kilns are 7 to 7.5kw, so what would I do?Is there perhaps some confusion with the 6kA breaking capacity of the OPDs in domestic CUs?