Yes...?Do you really think that clamping round N&L will show EARTH leakage?
these are also often built into PAT testers, but can't be found using a multi meter most of the time, a clamp on ammeter
may help, but either way hard for the non electrician to find the fault. I have all RCBO's which is a RCD and MCB combined so if some thing goes wrong, I don't loose as much, and earth - neutral faults are less likely to cause tripping.Thank you, appreciate that!1) An induction hob is an electronic device and may need other than a type AC RCD although mine seems to have no problem with a type AC RCBO.
2) You have a lot of circuits through the RCD, so it could well be a build up of leakage from many circuits.
However the most likely is an earth - neutral fault likely nothing to do with the induction hob, but as the hob draws high amps the voltage difference between earth and neutral increases, so also any leakage earth to neutral also increases, and this is causing the imbalance between line and neutral and causing the RCD to trip.
Earth to neutral leakage is normally found using a insulation tester View attachment 321265these are also often built into PAT testers, but can't be found using a multi meter most of the time, a clamp on ammeter View attachment 321266 may help, but either way hard for the non electrician to find the fault. I have all RCBO's which is a RCD and MCB combined so if some thing goes wrong, I don't loose as much, and earth - neutral faults are less likely to cause tripping.
So for you first thing is to unplug anything not in use, a bit of damp bread stuck in a toaster can cause the RCD to trip when kettle is used, if the toaster is left plugged in, as the switch on the toaster only switches the line, it does not switch neutral, so to switch neutral only way is to unplug.
For me it is easy, I have the testers and knowledge how to use them, but for you only thing I can suggest is unplug all items when not in use. Items which are double insulated are less likely to be a problem, one often they are double pole switched, and two no earth to leak to, but I really have never considered how to test for earth - neutral leakage without my meters, as never needed to do it.
Yes my house shows around 26 mA total, but that is shared between 14 RCBO's so no problem. However of the two clamp on meters shown, the yellow one only shows down to 10 mA increments so really not suitable for finding earth leakage, the red one do measure down to 1 mA increments, and is OK with AC, but on the DC scale testing for the 6 mA DC leakage not really much good as needs zeroing then not moved, and can't really do that over meter tails, so still a bit hit and miss with DC.Do you really think that clamping round N&L will show EARTH leakage?
Just out of interest, are RCBO's a straight swap for the ones I currently have in the existing CU?For example if I was to just swap out the Cooker circuit for an RCBO or one of the other circuits or are they a different physical size?1) An induction hob is an electronic device and may need other than a type AC RCD although mine seems to have no problem with a type AC RCBO.
Ok thanks for your help.I don't know that make of CU, a CU is a type tester distribution unit, and to retain the type testing only items sanctioned by the manufacturer can be fitted, or it stops being a CU. Also today most are metal and also have surge protection, maybe some one else will know if there are RCBO's for that box.
It would need the RCD removing for that way, which would likely mean new buss bars, or all the MCB's replacing with RCBO's and the RCD swapped for an isolator.
It does seem likely these will fit but I am not sure.
What shall I check if I do a deeper dive on them 2 appappliances
Thanks, just had a look at them and pretty sure my father in law has one of them so will have a word with him.There seems to be two options, get some one in, or DIY, and not sure which is best or cheapest?
A insulation tester cheapest I could find cost me £35, and you need one to test further. Easy enough to use, clip one lead to earth pin on plug and other to neutral pin, set to 250 volt and press button. One is looking for a reading over 1000000 ohms or one meg ohm.
But if you get some one in, maybe not only find the fault but can cure the fault.
Likely the problem is the mineral insulated heating element in an appliance. But really need to test, not change to see if that works.
Managed to get my hands on this today. He has this one https://amzn.eu/d/aFeNWvsThere seems to be two options, get some one in, or DIY, and not sure which is best or cheapest?
Ok thanks. Guess ill spend a bit of time tomorrow testing a few other plug in appliances and see if anything jumps outTesting neutral to earth is the main thing, as tripping with nothing turned on, and 1MΩ is a pass would would expect higher.