Room stat replace
22 Nov 2023
I have an old Satchwell TLX2356 room stat wired with a Honeywell k42008628 frost kit.
The wires in the room stat are
Yellow to terminal 1
Red to terminal 3
Blue to terminal 4
Both the Yellow and Red wires are constant live
I want to replace with a Honeywell DT90E stat , can you advise me on the correct wiring please.
3 = feed in
1 = feed out
4 = neutral
However it will work without a neutral so needs testing, Google TLX 2356 wiring diagram came up with the results, if you need some one to do that for you, I think time to give up.
I am sure the DT90E came with a wiring diagram.
As the DT90e is battery operated, the blue wire (probably neutral), currently in terminal 4, won't be required.
Safely isolate this in a separate terminal block, or Wago.
The red and yellow wires can then connect into terminals A and B.