Water hammer from unvented cylinder
You were seeing 8 bar on a (the) PG installed near the washing machine, do you expect 8bar there or can you put another PG on there again and note both pressures. Or you could remove the arrestor at the IGV and connect the PG directly here to see if you still get only 3.0/3.4bar or whatever.
Hi, I’ve done that before. Near the ICG it’s never spiked more than 5.
Not since I put the PRV in. More like 4.5 during a spike now.
Well, if you're pretty sure that the mains pressure is 4.5bar then those pressure spikes are normal enought IMO, I'd still like to see the ICG NRV operating "normally", not with a zero dP, but looks like you would have to remove the upstream PRV to achieve this.
I can't find a exploded view of a ICG to see the check valve in this but imagind its spring loaded to avoid chatter even under normal conditions.
I can't find an exploded view of a ICG to see the check valve in this but imagind its spring loaded to avoid chatter even under normal conditions.
Caleffi were confident it’s not the NRV. But the more I listen the more I think it’s the ICG
I don’t have the old one as I put it in the bin!
Trying to see this correctly - re the video of the gauge - there's one knock when the tap is opened and the water runs then another when the tap is shut and the water stops?
Not really - there probably isn't anything wrong with the valve in the control group, if it is being impacted by a pressure spike travelling along the balanced feed when a tap is being opened and the same being closed then that may be what's creating the knock at the valve.
May not be a problem with the valve, it's just creating that knock under these certain set of circumstances, wouldn't be the first time I've come across that. Again, bypass the valve to the balanced feed and see what happens
You said in your very first post in your Water Hammer thread that "I've noticed since the install was about 6 months old I'm getting a water hammer/knocking/clunking noise from my unvented cylinder whenever the cold taps in my house are open and closed."
Was the system trouble free for those first six months?.
Re Mixing/TMVs (thermostatic mixer valves), is any one of the cold valves, ie, say one on the (if installed) bath (cold tap) not fed from either a TMV or a manual mixer tap set and if so does it result in water hammer and that (ICV) PRV rattling?.
It depends on the time of day. I think if there's positive pressure from the HW connection it's not as loud