If it did trip, it would presumably be a faulty MCB ... a B45 MCB is required to carry 50.85A indefinitely without tripping and, even if the 11kW were quotes at 230V (unlikely), that would be under 48A.Likely an 11 kW shower will never trip a 45A MCB or damage the cable.
Agreed however other people also read the posts and with 6mm² cable feeding a shower with a B32 MCB quite often it is overloaded, but will still hold for long enough to get a shower. I have found, when this is the case over time, the MCB gets more and more sensitive, and the time one can shower for decreases as the years go on. Likely this varies manufacturer to manufacturer, it really will depend on the temperature required to trip the device, and if that is high enough to cause oxidisation, and so weakening the element.If it did trip, it would presumably be a faulty MCB ... a B45 MCB is required to carry 50.85A indefinitely without tripping and, even if the 11kW were quotes at 230V (unlikely), that would be under 48A.Likely an 11 kW shower will never trip a 45A MCB or damage the cable.
Kind Regards, John
Indeed, that can happen. However, in the context of your comments, at least in theory a non-faulty B45 should really never trip with a shower of 11kW or less, even if it were run continuously.Agreed however other people also read the posts and with 6mm² cable feeding a shower with a B32 MCB quite often it is overloaded, but will still hold for long enough to get a shower. I have found, when this is the case over time, the MCB gets more and more sensitive, and the time one can shower for decreases as the years go on.
Never heard of one so small - I can't see how it could ever have worked.Just to be a bit clearer, the electric shower being used is only 4kw
Not necessarily - the length might be too great given voltage drop for a larger load.and we are replacing it with a 10.5 kw in the same place, so the length of the existing cable is adequate for connection
As per mikeyd, why don't you believe that?We do not believe that the cable itself needs to be changed/upgraded which is what we are being told
As a matter of interest, what degree of voltage drop do you believe would "impair the safe functioning of" an electric shower?Not necessarily - the length might be too great given voltage drop for a larger load.
In practice, it obviously depends on what one's 'usual' supply voltage is. BS7671 deems any (no-lighting) equipment to be OK down to a "voltage at its terminals" of 204.7V, which represents ~15% VD for someone with a usual supply voltage of ~240V.I don't know. I do know that mine is full of electronics, and I don't know what voltage regulation is in place for those.
I don't. My copy of 525 talks about "the product standard relevant to the equipment (if there is one)" (whatever standard that might be for a shower), which may or may not specify a minimum voltage, but it says nothing about manufacturer's instructions.I don't know what the maker quotes as the minimum voltage for his shower. I do know what 525 says about that.
I'm not really sure why you're getting so excited. To be adequate, current-carrying-capacity-wise, for a 10.5kW shower, the cable would have to be at least 6mm², possibly 10mm². Even if one uses the BS7671 guidance VD figure of 5%, that would be satisfied by any cable length less than about 37 metres for 6mm², or about 62 metres for 10mm², cable lengths which I very much doubt would be exceeded in a normal house.So are we again facing the situation that when you don't KNOW something you are happy to GUESS and tell the OP that there IS NO CHANCE WHATSOEVER that an appliance where the maker specifies a minimum voltage won't work properly at a voltage below that?