hi.
i am replacing an old earth trip on a tt insulation.
i should had got a 100ma rcd, but by mistake i have a 30ma.
if i fit the 30ma rcd and it causes no problems is it ok to leave it or MUST it be a 100ma.
If there really are no problems then there is no regulation that says you cannot have a 30mA RCD as your main switch, but... All your lights will go out if you plug in a faulty appliance that causes the rcd to trip, or if you get a socket wet.. or any other accessory for that matter. 30mA RCD's are for supplementary protection from electric shock, but are prone to nuisance tripping, which is why most modern installations have a split load consumer unit. It's up to you, but I'd get a 100mA RCD for your main switch.
a 100ma rcd on its own is *NOT* ok on any TT system that includes sockets
while there are no wiring regs that prevent useing a 30ma rcd for the whole install it is considred very bad practice and may fall foul of other regs (stuff about continuity of supply to fire alwarms)
best practice with a TT is to use a time delay rcd (usually 100ma) for everything and a normal 30ma rcd to cover *ALL* sockets and any other high risk cuircuits
Sorry, you're quite right, Plug. ALL sockets on TT install must be 30mA RCD protected. Having mentioned a split load unit I was (wrongly) continuing down that route. Thanks for the correction
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local