They are triplets.I should have qualified that with "... until the new-fangled ones with Wago, or Wago-like' terminals recently appeared - but I think they they also only have 'pairs' (not 'triplets') of terminals.
Kind Regards, John
They are triplets.I should have qualified that with "... until the new-fangled ones with Wago, or Wago-like' terminals recently appeared - but I think they they also only have 'pairs' (not 'triplets') of terminals.
Kind Regards, John
No, rings are peculiar to the UK and some other countries using BS 1363 sockets.I read on FB today that in Canada/Aus there should be no more than 1 wire per terminal.
So they don't do rings then.![]()
I should have qualified that with "... until the new-fangled ones with Wago, or Wago-like' terminals recently appeared - but I think they they also only have 'pairs' (not 'triplets') of terminals.
Kind Regards, John
They are triplets.
OK, I stand corrected. That's a step in the right direction, then!mk <piccie>
Agreed, a circuit in BS7671 is defined as "an assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective devices" so yes it's one circuit by definition.It is still one circuit by definition
Indeed - as plugwash has said, the totality of any number of 'ring finals' protected by the same OPD constitute 'a circuit' by BS7671 definition.My ten pennorth. One two or three rings in one fuseway is still just one ring final circuit.
I see no reason, why not, since the considerations for each of the two 'sub-rings' are identical for the two rings - and, indeed the risk of "...the load current in any part of the circuit [being] unlikely to exceed for long periods the current-carrying capacity (Iz) of the cable." (as required by 433.1.204) is actually less with the 'two rings' than if the same sockets were all supplied by a single ring.The question is whether two rings of cable fed from the same breaker constitute a ring circuit and hence whether they benefit from the dispensation for ring circuits to use lower-rated cable than would normally be required for a given rating of breaker.
This is one of those points I've personally never understood: a DSSO on 2.5mm² installed directly from the MCB is:... No. If we see a simple ring with a spur at the origin we would accept it, if we then remove the ring and just leave the "spur" it has not become any worse for overload or short cct etc.
433.2.2This is one of those points I've personally never understood: a DSSO on 2.5mm² installed directly from the MCB is:
Perfectly safe and acceptable within the regs if there is something else connected to it but
Is not perfectly safe and acceptable within the regs if there is nothing else connected to it.
433.2.2
Presumably you mean from a ≥32A MCB, yet that is a rather strange thing to say.
"You have never understood why something perfectly safe and acceptable in the regs is not perfectly safe and acceptable in the regs."
What led you to that misunderstanding?
Indeed.This is one of those points I've personally never understood: a DSSO on 2.5mm² installed directly from the MCB is: Perfectly safe and acceptable within the regs if there is something else connected to it ...
Who/what said that? As far as I can see, 2.5mm² (Method C, hence CCC=27A) protected by a B32 (which will inevitably provide adequate 'fault' protection) is OK per BS7671 if it is protected, at worst, with 26A worth of downstream fuses (2 x 13A plug fuses).... but ... Is not perfectly safe and acceptable within the regs if there is nothing else connected to it.