BS1363 does not require double adapters to have a fuse. So with two unfused double adapters in a double socket you could potentially have four plugs with fuses adding up to a total rating of 56A.Indeed.
at worst, with 26A worth of downstream fuses (2 x 13A plug fuses).
But more generally, outside of the specific exceptions for rings, is it acceptable to rely on overcurrent protection that is not part of the fixed installation to protect the fixed wiring? I know the informative appendix suggests that a 20A rated spur from a 32A radial is acceptable but is there anything in the normative part of the regs to back that up?
The whole system of BS1363 sockets and the circuits that supply them is ultimately built on the assumption that load will be spread around it's unlikely that two (or more) full-sized loads will be connected and used in the same location. BS1363 only requires double sockets to be tested at a total of 20A and BS7671 only requires cables in rings and spurs to be rated at 20A.This is one of those points I've personally never understood: a DSSO on 2.5mm² installed directly from the MCB is:
Perfectly safe and acceptable within the regs if there is something else connected to it but
Is not perfectly safe and acceptable within the regs if there is nothing else connected to it.
That IMO makes a double socket alone on a 32A circuit questionable design regardless of the cable size. At best it's a breaker that is larger than it needs to be for no good reason. At worst it's encouraging people looking for places they can get more power to overload the socket.