3 phase generator output
14 Sep 2004
having a discussion with someone about how many amps per phase will i get out of an 80KVA, 3phase genny - and we both get different answers. i get 92.75A, he gets 160A.
my way: 80KVA x 0.8pf, 64KW, /230v = 278.26A /3 = 92.75
his way: 80KVA x0.8pf, 64KW /230v = 278.26A /1.73 = 160.84A
So, are any of these right?
You're both wrong - 80kVA is 116A per phase @ 230/400V
Which is the maximum current the genny can provide
I think it depends on the situation, what I think the manufacturer is saying is that it can produce 80KVA when given a load with 0.8 power factor so if your load has a power factor of 0.8 then your limit will be what ricicle says but if your load has a power factor of 1 then it will be what you say.
Your friend is just plain wrong
When looking at the kVA rating of a genny this is refering to the maximum current it can supply at rated voltage.(VA)
Thus 80000/ (1.73x400) = 116A approx per phase
Depending on the power factor of the load will depend how much of this current is doing actual work (real power - kw) and how much is contributing to reactive power (KVar)
@ Unity PF I had 115.47 but I did go the whole hog and use 1.732
Is the quoted 80kVA prime or standby power because that has a big influence on what you actually draw for any length of time.
where does this 1.732 come from?
i thought it was x0.7... or is that to get power per phase from 3 phase KW?
nevermind, it's sqrt 3.