Yes, I don't know where I got 17A from, either for each lead or a cockup on the arithmetic front.
I said it, thats what it works out to with diversity
I haven't done any actual calculations, my 'in head' guesstimate is based on 4½A/KW or about 32A total or 16A each (assuming the 2 terminals carry equal loads) , then diversity which I guestimated as under 20A would be 10 + 22/2 or 17.33 so I was a tad high there.
However the vast majority of my work has been commercial where for a start diversity is not normally applied, a 7.4KW load would automatically be 6mm² minimum (in fact 4mm² would only be considered for a circuit near the top end of 2.5mm² CCC) - calculated as 7400/230=32.17A (or bothering to calculate for the stated power at 240V would be 29.55A) for a cooker that would be 32A OCPD, if there was a 3KW oven to go with it that would most likely be an additional 16A/2.5mm² circuit. I'm not referring to a commercial kitchen here, for example a caretakers appartment in an office block or the office tea room.