In 1954 when my parents house was built, there were demarcation lines, unions would not let electricians to do plumbing work, or plumbers to do electrical work, so the supply to the immersion heater went into a 15 amp socket and the immersion had a 15 amp plug so the plumber did not have to do anything other than plug it in once fitted.
The 15 amp socket went to a 15 amp fuse in the fuse box, and was a dedicated supply, and since no fuse in the airing cupboard there was nothing to produce heat.
Moving to using the 13 amp plug and socket, would result in there being a fuse in the plug, and a fuse clearly has enough heat to melt the fuse wire inside it, so must always be in free air, or fan assisted air with a built in oven. In the airing cupboard hard to ensure free air, so need the wall to dissipate heat, so need the fused connection unit, so it is built into a wall and can get rid of the heat.
Or of course a cooker connection unit could be used, and a 16 amp MCB/RCBO in the consumer unit.
However with a radial supply having an immersion heater on the supply worse case scenario is it may together with other items cause the MCB/RCBO to open.
A 2kW load will never overload one leg of a ring where ever it is fitted. At just over 8 amps it is far less than the rating of 2.5mm2 cable. There is no reg saying loads over 2kW have to go on their own circuit either.
That is true of course, but I did not think I had to add "together with other current using items" and this is the problem with the ring final, designed to use 7/0.029 cable, but latter we reduced the size to 2.5 mm² and increase the overload setting from 30 to 32 amp. In the main this is not a problem, as cable still rated 20 amp or more, and two cables so cable good for 40 amp, and overload set to 32 amp.
However we are permitted around 106 meters of cable, (was from memory 88 meters) and if we have a number of items near the origin of the cable we can get over the 20 amp on one leg, but as long as the items don't run for long, this is not a problem, it takes time to heat up the cable, and a kettle at 3 kW runs for such a short time, the cable does not over heat, I know I switch on two cup boilers powered from the same 13 amp fuse, to make 2 cups of coffee in the adverts, and it does not rupture the 13 amp fuse.
So we are looking at both overload and time, and only with a ring final, if using 20 amp radials it does not matter. Only with a ring final can there be a problem, and at 15 litres using
this calculator it says it will take around 50 minutes which is less than the time set with tumble driers, so either tumble driers need a dedicated circuit i.e. not on the ring final, or your heater is OK on the ring final.
So personally I think OK on a ring final, but I have tried to show why I feel it is OK. Rather than make some unhelpful statement like.
A 2kW load will never overload one leg of a ring where ever it is fitted. At just over 8 amps it is far less than the rating of 2.5mm2 cable. There is no reg saying loads over 2kW have to go on their own circuit either.
I had already stated "it suggests" not the regulations say, and "appendix 15" OK missed it was quoted from the 2008 edition. I was trying to show why some one would consider not permitted, rather than simply say they are wrong.