Hi, Does anyone know if the smoke detector circuit on an Accenta G4 needs an EOL device. The panel manual does not mention EOL but a small diagram hints at a normally open circuit. I wouldn't need an EOL if thats the case but I think the circuit is NC. But still not sure if I would need EOL. The sensors are Ei100R3. Its not been powered up yet so not been able to test it out.
 
Sponsored Links
Hi Meadowhog,

If you program either zone 7 or 8 as fire alarm on the Accenta G4 you don't need EOL resistors. The circuit is only looking for a normally closed input.

Regards

S.A.F.
 